asked in Thermal by (215k points)

         An R717 based vapour compression refrigerating machine works between 38°C and –20°C temperatures. The ammonia leaves the compressor dry and saturated. Liquid ammonia is under cooled to 30°C temperature inside the condenser, before throttling. Find the theoretical COP of the machine. The cP of saturated ammonia liquid is 4.91 kJ/kg-K. if net refrigeration required is 25.0 TR, find the mass flow rate of ammonia in kg/h, assuming relative COP 0.75. The saturation properties of R717 are given in the following table:

 

Liquid

Vapour

t, °C

h, kJ/kg

s, kJ/kg-K

h, kJ/kg

38

380.78

1.6134

1489.36

–20

108.55

0.6538

1437.68

 

Please log in or register to answer this question.